Default Sprinkler

Wet Sprinkler System

System side pressure and supply side pressure are the same? Do you guys know what's causing this? Also, it's equipped with a backflow preventer. I suspect this might be the cause but wanted other opinions. Also, what is the solution? conducting a 2 inch drain test?
Reply With Quote
  #2  
Old 07-30-2010, 03:47 PM
CKL958 CKL958 is offline
Senior Member
 
Posts: 315
Default

Quote:
Originally Posted by surewin View Post
Wet Sprinkler System

System side pressure and supply side pressure are the same? Do you guys know what's causing this? Also, it's equipped with a backflow preventer. I suspect this might be the cause but wanted other opinions. Also, what is the solution? conducting a 2 inch drain test?
If an attempt has been made to bring the system pressure up and it does not rise, you have a leak. I wouldn't so much suspect the backflow as a leaking drain valve, or a gasket on the flapper not seating properly. The backflow is on the city side of the system - it will have no effect on the building side of the system holding pressure.
__________________
CKL958

"We're all in this together"
- Steve "Red Green" Smith
Reply With Quote
  #3  
Old 07-30-2010, 06:35 PM
infernobuster infernobuster is offline
Resident trouble maker
 
Posts: 387
Default

A few things i would check ..

- a possible leak at the inspector test site
- a leak in the system itself
- bad jockey pump or bad jockey pump lines
- faulty gauges ( they have to be swapped out every 5 years)
__________________
All men are created equal, a few become fire fighters.
Reply With Quote
  #4  
Old 07-31-2010, 12:36 PM
sugar sugar is offline
 
Location: BC
Posts: 57
Default

is there an alarm valve or just a manifold with a flow switch and test and drain? New or old system??
Reply With Quote
  #5  
Old 07-31-2010, 04:32 PM
gfd31 gfd31 is offline
vollieff31
 
Posts: 52
Default

What is the "system pressure" supposed to be?

It is possible to have both the "city pressure" and the "system pressure" to be the same, or relatively close.

If there was a leak, or even a problem with the backflow preventer the system would have "flow" and the alarm should be sounding, and if it's connected to a fire alarm system you should have either a supervisory or a trouble on the FACP at the very least.
Reply With Quote
  #6  
Old 07-31-2010, 05:48 PM
CKL958 CKL958 is offline
Senior Member
 
Posts: 315
Default

Quote:
Originally Posted by gfd31 View Post
If there was a leak, or even a problem with the backflow preventer the system would have "flow" and the alarm should be sounding, and if it's connected to a fire alarm system you should have either a supervisory or a trouble on the FACP at the very least.
Flow switches generally wouldn't trip for water travelling backwards in the system. They are a spring return paddle that closes contacts when pushed. Therefore, water travelling towards the city would be pushing back to the "normal" position, and would not cause an alarm.

In a system that utilizes a pressure switch on the alarm line to detect flow, the main alarm valve would have to be open to allow water into the alarm line to create an alarm.

The backflow would be the absolute last place I would be looking. The pressure has to leak through the alarm valve to pass back into the city supply.
__________________
CKL958

"We're all in this together"
- Steve "Red Green" Smith
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Forum Jump


All times are GMT -8. The time now is 05:49 PM.


Powered by vBulletin® Version 3.6.8
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.